Equipment: Norcold Model No. N180.3R
Serial No. 27370072
My overhead view of my frig
We bought this rig the last week of May, took
it out right away, frig worked on all 3 modes.
NOW:
3-way Norcold N.180.3 in a 2018 320S almost
perfectly level
We tried to get it to warm up to make the chemical reaction to make the frig cold. Nothing Happens
AC: Shore power turned on nothing happens, yes frig set to shore power, we see the little green light on the frig control panel, the 20 amp breaker is not tripped.
DC: Battery is new, and plenty of amps, 13.8 on the battery per the volt meter
Propane: Propane Tank ¾ full.
Propane tank turned on checked this by turning a burner on the stove top.
After a few hours, no heat coming off the outside heat vent…certainly no cooling, yes frig set to coldest.
Mechanic said NO SPARK when I push the ignite button.
All three methods for getting Mr. Norcold to get cold are not successful..
Currently: Fuses/Breakers not-tripped, all plastic fuses checked for signs of burnout, all appear normal.
Frig is currently on shore power (30 amp) and is getting power, per the
green plug icon on the control panel, no heat coming from the outside vent
I am open to suggestions / tests or documented procedures for checking this beast to find out what is broken. .
I just bought a bag of glass fuses for this beast.
Comments
Following this post- no doubt- other T@Ber's references to countless electric only refrigerator replacement options! Perhaps inevitable...
For troubleshooting purposes set the fridge to battery with shore power disconnected. You should measure a noticeable voltage drop at the battery. This indicates the heating element is working. You can reconnect shore power and leave the fridge on DC for a few hours. If does not cool down the cooling unit has lost its pressure.
If that checks out, test the AC heater. *Disconnect shore power* and measure resistance across the AC heater. The wiring diagram is on top of the fridge. It should measure sub-100 ohms.
Problems with gas operation can indeed be the igniter. IIRC it is not possible to remove the wire at the igniter so you'll probably need a way to look inside the burner box. Sorry can't be more specific, I have the older style fridge.
. . . suggest you follow the NorCold Troubleshooting Flow Chart for 120VAC Operation (below).
TV: '17 Colorado V6 Z71 4x4, Tow Package, GM Brake Controller
Adventures: 54 Nights: 341 Towing Miles 43,780
It is the same design as the N180.3 at least for the 120VAC. See Here, the first post has the full Service Manual of model-3136.
With a bit of 'user logic' you could use the Propane Flow Charts to troubleshoot the N180.3 . . . just remember the N180.s uses a Different Ignition Method