I wrote to Battleborn, curious about what gauge wire they recommend as I added a second of their 100ah batteries to my trailer. Took longer than I’d hoped to get an answer, but they shared a picture that I thought was useful. Only question I had was about the 200a fuse. I think my tab version of that is the glaso 40a?
Comments
My simple understanding is that the 1200 continuous watts inverter would produce 120v up to a max of 10a of a/c. That’s 120 watts at 12v coming from the battery (85% efficient).
- the 4ga wire is at the edge of its ability. And running hot as heck.
2015 Audi Q7 TDI
Northern Ohio
I contacted NuCamp support about adding a second 100 ah Battleborn battery to my 2023 400. Will the 4 gauge wiring and 150 amp fuse handle this additional battery?
Here is their response:
"Yep, that will be fine as you are just adding a second battery for capacity - the voltage will not change.
So you will want to make sure to wire the new battery in parallel - this will keep the same voltage (12V), but double the amp hour capacity.
You are essentially just adding more battery amp hour capacity, and not changing the flow / voltage that comes from the battery/ies."
2015 Audi Q7 TDI
Northern Ohio
Considering a 2024 TaB 400 with all the option packages (full lithium),
2023 Jeep Gladiator Sport S, Max Tow Package.
Ken / 2023 Tab 400 “La Bolita” (23,000+ miles) / 2024 Toyota Sequoia
2024 - 3 Trips - 35 nights - 9 National Parks, 3 National Forests
The loads are not changing when more batteries are added. What does change is the max current that the battery system can demand when charging. The internal resistance of the batteries is in parallel and is halved when a 2nd battery is added. From experience I can say the 40A GLOSO breaker will trip after a few minutes when passing 52A. I did not have an issue charging from say 30% state with a single battery, but when I had discharged pair of Lithiums to a similar state I hit the 52A mark. This was the max that the 8955AD (WFCO) would put out. A 10ga wire can handle 55A when the insulation (wire coating) is rated to 90C, but 40A if limited to 60C which is typically what is quoted in tables. I changed the GLOSO to 50A version. This current is flowing from the 8955AD charger to the battery and that is the path of interest. UPDATE: After typing the above I rechecked the wiring from the WFCO through the disconnect, GLOSO breaker, and to the battery. It is 8ga with 105C rated insulation in my 2023 T@B400 and the wire is not bundled (close bundling lowers the rating). There is zero concern to up-spec the breaker to 50A (or a little higher) as there is lots of headroom in this wiring path to the batteries. The wiring to the solar panels is thinner and fused appropriately.
If you change the load on the batteries by beefing up the inverter (for example), then you will want to scale the fuse and the wiring to something appropriate. If you don't change any loads, then you won't have to do anything.
2023 T@B 400 Boondock "Running up a T@B"
Jericho, VT
1/0 for the combined current path is a bit of overkill; 2ga would be fine (Heck though the likelyhood you would be sourcing enough sustained current to have a problematic voltage drop or enough heat in even 4ga wires is hard to imagine). You would not have to change the fuse or the wiring to the inverter. The fuse is sized to protect the inverter and is independent of the capacity of the power source. The GLOSO breaker is sized to protect the wiring (and is quite conservative). I am open to commentary.