I’ve had a SoftStart installed on our 2021 400 for three years and it has worked with no issues at all sorts of elevations.
We just went on a weekend trip and I wanted to run the AC. I have a Westinghouse iGen2500 generator. My surge protector (hard wired) would trip and report that the voltage had dropped below 109 volts and wouldn’t allow the AC to start up.
I considered elevation (which was about 8k feet) to be an issue even though I’ve used it at higher elevation without issue.
So back home where I know the generator will run the AC without the soft start I tried to run it and it also would trip the surge protector and cut power.
So I’m wondering if the generator is the problem or the soft start? I can run the AC fine on a 20a circuit in my house. This is the first generator I’ve owned but I assume lack of maintenance could contribute to loss of power? It only has 50 hours on it and I’ve changed the oil annually. I have never cleaned the carb or anything like that.
Comments
2018 TAB 320 Boondock (previous)
Odessa, Fl.
I do have a ground plug jumper as the Watchdog won't even work without one.
I keep thinking it has to be the generator that's the issue.
2020 Tacoma TRD Off-Road
Minimum sized equipment saves expense, weight, and space. The down side of minimum equipment is the need for it to work perfect all the time. I may suggest 3300 or 3500watt generator to have some head space when the world is not perfect. The advertised ratings are often surg rather than continuous power.
Storage and motors don't like each other. If the generator hasn't been used for 2 or 3 months, it needed to have all the fuel drained before storage or cleaned out after. I normally do the after; although, following the manufacturer's procedures for storage is the better practice.
Loading the generator up with a space heater or hair dryer is a good idea too. But, you have already confirmed all the other parts are working. It's internal inverter may hide the brown out condition. A low voltage warning, working when on external power, plus a winter without maintenance makes me think the generator is at fault.
"Just Enough"
2020 Tacoma TRD Off-Road
Replace fuel lines, filter and the carburetor gasket(s). Clean or replace the spark plug. Most parts houses have a "Tune Up Kit" that has most of the parts for less cost than separate purchases.
Your Westinghouse 2550 is "2550 watts peak." It is only 1800 watts continuous at sea level, 1900w for the duel fuel model, when new (see owners manual). As you go higher in altitude, you loose about 3% per 1000ft. To get the power from a normal home extension cord at the altitudes you are camping, you need a bigger unit or spend a lot of time tinkering with the generator.
"Just Enough"
2020 Tacoma TRD Off-Road
SW Montana USA
2020 Tacoma TRD Off-Road
Although the generator has a "30amp" plug, it only puts out 1800watts (about 16amp at 110v) minus the altitude loss. Your generator is just equal to an extension cord when perfect at sea level.
For keeping the battery charged, your rig is great. Camping in the heat of summer will get a little sketchy some days. I do understand the significant size and weight increase when you step up to the next level. We all make these decisions. My choice was "boondocking = no AC". I've gotten creative with a canopy for the trailer...
"Just Enough"
@Mickerly No 30amp outlet but this is 100% a generator issue. I ordered a new carb and will see if that fixes it. I wasn’t the best about maintaining fresh fuel in it but the carb didn’t look particularly dirty.