2022 Tab 320s
Is there a unique fuse for the glycol pump in the 3020?
I was getting hot water but no heat about a month ago. I couldn’t get the glycol pump to turn on, even through setting it into continuous mode. I took it to a Truma authorized service center and they replaced the pump. I picked my trailer up this morning. Service rep told me that the techs had tested everything and it was working fine. I get it home and I still can’t get the pump to turn on. There are no error messages on the screen, the glycol is heated up to 170 F. I have the heat cranked up to 80, and it’s 50 outside and inside the trailer. I opened the overflow expansion access and the glycol in it is cold. So the glycol is definitely not circulating.
I bought my trailer new and have done the glycol changes as directed every two years. Last change was this summer. I hadn’t used the heat until last month when I needed it, so I’m not sure if the pump ever worked after the glycol change.
Comments
If the Cont setting turns on the icon then the pump settings can be checked on the pump itself. 2-3 is the normal operating setting. It might be turned all the way down.
Final idea is an air block in the loop preventing flow. Try turning the pump to 5 to clear this. This setting should cause visible churning in the reservoir tank, confirming the pump is working.
If all this fails then back to the technician or email Truma. Found one fuse thread with the Truma email here
https://tab-rv.vanillacommunity.com/discussion/18269/alde-3020-thermal-fuse
2019 T@B400 Boondock Lite "Todd"
Continuous setting doesn’t get the pump going.
2019 T@B400 Boondock Lite "Todd"
Also there is a reset procedure (actually two) for the Alde system. In the settings menu of the screen on page 4 should be a reset button. Or disconnect both shore and battery power for 10+ minutes supposedly works too.
2019 T@B400 Boondock Lite "Todd"
The pump is turned to continuous and set to a speed of 5.
The outlet the pump plugs into reads 12.5 V.
I did a hard reset unplugging the 12V and shore power for 30 minutes. I also did a reset off the control screen.
I still can’t get the pump to turn on.
It sounds like a power issue to me. Maybe inspect the length of the wires along the distance from the from the circuit board where the cable plugs in, and down to the pump, looking for any breaks or damage to the wiring (although I believe the two wires may be covered with an electrical wrap, so not visible). With AC/12V connected, jiggle the wires at the pump to see if anything happens. Also, maybe probe the two wires with a multimeter to determine if power is present where the wires enter the pump.
(Alde: 3020; Refrig: Isotherm Cruise 65 Eleg; Battery: BB 100Ah LiFePO4; Solar: Renogy 220W Portable Suitcase w/ Victron SmartSolar MPPT 75/15 Controller; Victron BMV-712 Battery Monitor w/ Shunt; Pwr Cntr: PD-4135KW2B; EMS: PI-HW30C)
Greg & Marlene (Tucson, AZ)