I know this topic has been widely discussed on this forum, but please humor a guy trying to do some electrical engineering math. I have a 2020 Tab 400 with the 6V batteries in the extreme back of the trailer and the power distribution center (with charger) underneath the front right bench seat. Conservatively, there is 25 feet of 8 AWG wire for the charging circuit between the distribution center and the terminal block close to the batteries. Multiple occasions have shown it to be impossible for me to bulk charge the batteries with a generator while boondocking.
Because of the wire size used and the distance to the batteries, I would never get anywhere close to the 55 amp capability of the charger to the batteries, and the charger cannot properly sense the voltage of the batteries, so the charger never enters Bulk mode charging. Yes, I have seen other posts about people relocating the charger next to the batteries, but gosh darn it, we should not have to do that, and it comes with some trade offs I would prefer to not have to deal with.
In order to see what wire gauge would be needed for the batteries to get the maximum out of the charger, I did some math to calculate the CM (circular mils) of the 12V wire needed to deliver 12V 55 amps approximately 50 feet (distance of the + and - wires) assuming an allowed 3% voltage drop per code:
CM = (12.9 x 55A x 50’) / (3% x 12V) = 98,542 CM
Then cross-referencing the CM with AWG chart, it says I would need 1/0 AWG wire for that amperes/distance/V drop ! If one looks at the chart for the 8 AWG wire actually used in the camper, the max amps allowed for that length of circuit would be 10 amps.
Any EEs see anything wrong here?
Comments
When it comes to the charging time issue (because in reality the WFCO charges the batteries, it just takes extended time to do so), there are several factors at work.
I am attaching a copy of the post that @rh5555 made several months ago regarding the issues and how to overcome this. Roger done all of the hard work, I done the simple task of buying a Progressive Dynamics converter from Amazon along with the removal of the OEM WFCO.
If you spend all of your time camping with electricity available to you, this upgrade (or fix) will mean nothing to you. For those of us who like to be "remote", it makes all the difference to be able to charge batteries with a generator in 3 or 4 hours VS. 24 to 48 hours.
My estimate is that you will spend around $275.00 to resolve this and would include the following items (or similar):
PD9260CV Converter with remote pendant - Amazon
1 x 4 gauge black battery cable with a 3/8" lug - Auto Parts store or Amazon
1 x 4 gauge red battery cable with a 3/8" lug - Auto Parts store or Amazon
1 x 120 volt dual RV outlet (they clamp on the wire, I got mine at camping world because I was there)
Installation is simple, there are 5 steps.
Replace the single outlet on the curb side under the bed with the dual
Mount the new converter to the floor with 3 screws
Cut the red and black cables to the proper length to reach the battery junction block
Modify the battery junction block cover to make room
Remove the factory converter form the power center, there are 2 screw and 5 wires to disconnect
Start to finish it will take you about an hour and will resolve your "charge time" issues 100% regardless of the battery chemistry you are using.
The only reason I suggest the PD9260CV is that in the future if you wish to upgrade to lithium battery technology (once again, only needed for your remote campers) you will not have to change the converter again. You merely force the Boost Mode with the pendant to charge your lithium batteries.
Brad
2022 Black Series HQ19 aka "Cricket"
2021 F-250 Tremor with PSD aka "Big Blue"
Concord, NC
If your system requires/accepts very high currents, many high rate charging systems have a remote voltage sense feature independent of the current carrying cables allowing monitoring and control based on the voltage at the battery (or load) terminals. This feature allows the control of voltage at the battery independent of any losses in the power cabling.
The OEM installed WFCO is rated at 55 Amps even though in the NuCamp build along with the operating characteristics of the the WFCO it will never enter the Bulk Charging Rate. The Bulk Charging Rate is 24.55% of the 224 Amp AGM battery capacity.
The PD9260CV is rated at 60 Amps, so the Bulk Charging Rate is 26.78% of the 224 Amp AGM battery capacity. With locating the converter closer to the batteries and lower resistance in the charging circuit the converter can use the Bulk Charging Rate. The second thing is with the pendant and Boost Mode, you can force the Bulk Charging Rate anytime for up to 4 hours. It is this feature that will allow this converter to be used with lithium batteries if an upgrade is made.
I have looked at several studies that compare using 20% to 40% of Amp Hour charging rate of the batteries being charged. I think this is more of an issue with lead acid batteries due to the potential of gassing than with AGM. And of course, as the lead acid batteries degrade with age and use this becomes a much greater issue to contend with.
I have not reached out to Harris regarding this upgrade or their allowable Charging Rate but I suspect that when NuCamp spec'd the components for their build that their engineering team did. With this being said, I wouldn't lose any sleep over adding an additional 5 amps of Charging Rate.
In closing, I would like to stress again it is my opinion that this upgrade, modification, or fix only benefits those who camp without utilities IE boondock. If you are primarily stay at resorts, parks, or campgrounds with electricity there is minimal benefit in making this change or upgrading the batteries to Lithium.
Brad
2022 Black Series HQ19 aka "Cricket"
2021 F-250 Tremor with PSD aka "Big Blue"
Concord, NC
I was considering if it made any sense to leave an upgraded charger in the distribution center and upgrade the wiring back to the batteries. Apparently the wire size required for that distance/amperage would be too large for the lugs on the charger.
Keep in mind that the higher the rate of charging the less efficient the uptake of stored energy. One reference I found stated 5 hours at 20% charge rate only yielded 60% SOC in AGM batteries. Once the batteries reach "absorption voltage" charge rate becomes voltage limited rather than current limited.
I gather when you refer to boondocking requirements, you are referring to generator charging through the onboard converter and are trying to limit run time. Possibly a sperate input port for the 12v output from the generator would be the most effective solution.
This is an interesting, well documented series of experiments a sailor did that provides some practical
https://pbase.com/mainecruising/effect_of_charge_rate_on_agm_battery&page=2
I do have a portable charger that I intend to wire directly to the batts for the next boondocking trip, and I will likely bite the bullet later this year for a remote converter + BB lithium solution as it is not feasible to upsize the wire enough to overcome the resistance/voltage drop from the distribution center.
Here is a link to their website for WFCO (sorry not WACO that is a town in Texas) Model WF-8955 that was installed in our 2020 400 BDL from NuCamp.
https://wfcoelectronics.com/product/wf-8955-55-amp/
It is the resistance as per the my earlier post that is the root cause coupled with the programming of operation of the WFCO that is the limiting factor on amperage and NOT the converter.
Here I quote from Rogers extensive testing (@rh5555) the first few sentences of the test results.
WF-8955 Operation in the 2020 TAB400
"There are 3 modes in which the WFCO WF-8955 converter can function, “bulk”, “absorption” and “float”. In any of these modes, the converter will provide up to 55 Amps of charging current, but the 3 modes are differentiated by how high the drive voltage of the converter can get:
Mode
Maximum Voltage
Bulk
14.4V
Absorption
13.6V
Float
13.2V
When 120V is applied, the WF-8955 converter senses the battery voltage before applying any charging current and makes a decision based on this voltage: If it is below 13.2V (which will almost always happen), then the converter attempts to initiate "Bulk" charging. In this mode the converter will push up to 55 Amps of current into the battery (while not exceeding 14.4V drive) and measures the battery voltage at the converter. If the charge current has not reached the converters limit (~55 Amps) or the voltage at the converter is above 12.8V the converter immediately moves to “Absorption” charging."
At the lower drive voltage, the amperage drops off like a rock due to the fact that the "sensed voltage" is close to the drive target which is interpreted as being nearly fully charged.
As far as using a 12 volt output from a generator both generators I have owned were rated at 8 Amps maximum output and NOT regulated, which means you would need to use a charge controller if you were to attempt this type of connection. Although I have owned Predator only, the Honda generators are set up the same and I would suspect that the others (champion, etc.) are similar also. So, you can use 8 amps and run forever to try and charge batteries or plug it in to a system that has the capability to charge at a higher rate. This is also where you are mistaken, I can easily get 58 Amps from my converter going through the shunt for the BMV-712, which completely busts your comment "Only the big industrial type quick chargers put out 50 or 60 amp charging amps."
For our use, once again we rarely have access to shore power making this simple and relatively inexpensive change to the converter was a game changer. We regularly end up with lots of tree cover (on purpose) and don't get enough sun on the solar panels to make it up daily.
At the end of the day, everyone needs to make a decision based on their use case scenario and more importantly correct and factual information. I would encourage anyone contemplating this to read the attachment in the earlier post that I made, again kudos to @rh5555 for doing the hard work of the testing and documentation. I didn't do anything but read his results and make a decision based on the "correct factual information" provided.
Brad
2022 Black Series HQ19 aka "Cricket"
2021 F-250 Tremor with PSD aka "Big Blue"
Concord, NC
cheers
My goal is to always try and provide as accurate of information as possible when posting on electrical-mechanical so that other forum members can use that to aid in making decisions or repairs that are appropriate for their needs. I am far from being always correct both in content and political correctness and I have been known through my working career (recently retired and I highly recommend retirement) for being honest, open and unfortunately blunt sometimes.
Brad
2022 Black Series HQ19 aka "Cricket"
2021 F-250 Tremor with PSD aka "Big Blue"
Concord, NC
The 2018 TaB400 came originally with one 200/224 Amp battery, located in the front of thr pax side rear storage locker (under the bunk next to the galley). The WACO is under the wardrobe closet. Sometime after Jan 2018, nüCamp switched to two 6VDC batteries in series to get 12VDC, so 2019 models got a sealed two battery locker in the same place as the single battery in 2018. When nüCamp switched to the Air8 in 2020 model, the batteries were relocated to the center rear under the bunk, behind the Air8 unit which was under the center part of the bunk (previously a storage area).
I agree we should always try and provide as accurate of information as possible when posting info here, and when I get a bit wrong, I appreciate being corrected.
Electrical systems are not something you want to get wrong, or major damage could result.
This from Bluesea, a marine electrical supplier:
B Find circuit LENGTH IN FEET along the left side of the chart. Note that the total length of the circuit is the roundtrip distance from power source (usually the battery) to the product and back.
This from Enginering Toolbox:
Wire Gauge Design Procedure
cheers