2018 Tab 400: fire up the alde system-lower desired heat way below ambient-elec at 2, gas is on-deck service menu, glycol and sanitary temp ambient. No Hot Water!
Turn desired heat above ambient-circulation flow starts-elec and gas same settings-flow circulation is indicated-service menu indicates glycol and sanitary above 100: Hot water!
doesn’t last long due to possible mixer thingy issue, still sussing that out-problem for another day.
why no hot generated with heat off??
0 ·
Comments
Is the Alde pump set to Therm? You want to avoid continuous as that will reduce hot water temp.
If the glycol is not heating then the Alde (heat source) is not turned on.
My Guess for the failure you outlined:
With Electric set to '2', propane in stand-by and No Cabin Heat Requested; no hot water.
When Cabin Heat is Requested the glycol/water was heating/hot.
So the Adle Electric heaters are not turning on. When Cabin Heat is requested the Adle knows it
has no 120VAC and switches to propane.
Unknown is why the Adle has or thinks it has no 120VAC.
TV: '17 Colorado V6 Z71 4x4, Tow Package, GM Brake Controller
Adventures: 56 Nights: 379 Towing Miles 47,220
will check the fuses!
Is the electric plug icon visible on the Alde control panel screen?
(Alde: 3020; Refrig: Isotherm Cruise 65 Eleg; Battery: BB 100Ah LiFePO4; Solar: Renogy 220W Portable Suitcase; Victron BMV-712; Pwr Cntr: PD-4135KW2B; EMS: PI-HW30C)
Greg & Marlene (Tucson, AZ)
Things to consider doing:
1] Do a hard reset of ALDE by turning ALDE off at the control panel, setting the battery
cut-off switch to Off and shore power disconnected.
Wait 3-5 minutes, reconnect shore power (battery optional), turn on ALDE and do your
Hot Water only test.
2] Turn Off the Propane Gas at the Control Panel. Force the ALDE into electric only mode.
Now do your Cabin Heat Requested test. With the propane set to off the ALDE should not
automatically switch to gas . . . . if the electric heaters aren't working (as suspected) then
the glycol will not heat. {or you may get a useful error message}
3] Listen to the main boiler PCB relays ( maybe a two person job )
Start with Control Panel Electric at '0' Off and Propane at Off.
Switch Electric to '1' and then to '2'
In maybe possible (ALDE service manual suggests it is) to hear the 120VAC Heater Relays Click On
At Electric '1' two of the relays will activate, at Electric '2' the third relay will activate.
If no clicking is heard - - - - possible Boiler PCB needs replacement.