Last year we replaced the stock 6V AGMs with two Aolithiuim 100Ah batteries in our 2022 Tab400 BD. I've recently noticed the solar controller is spending way too much time in float mode and being pretty ineffective in recharging our batteries. The solar controller sees the state of charge in the batteries as almost 100% so switching to float would make sense. However the Aolithium's app shows the batteries at 84%.
I do not have a background in trailer electrical (or any electrical for that matter) but can anyone suggest why the solar controller and BMS disagree on the battery voltage? Is there a way to sync them up?
Thanks in advance for any advice.
Glen & Karen | 2022 T@b400 BD | 2017 Toyota Highlander | Ottawa, ON CANADA
0 ·
Comments
Thanks!
I updated my Victron controller with the parameters from the Battleborn page but little changed unfortunately. It switched to bulk initially but soon returned to float. The solar controller is still seeing the batteries as fully charged (13.5V) while the BMS has them at 73% (13.11V). I'll continue my research but would appreciate any other thoughts.
(a) disconnecting the power from the Victron system/battery monitor, waiting about a minute, and then reconnecting the power to see what happens. A system reset, like when restarting a computer, can often resolve issues like you are dealing with.
(b) disconnecting the batteries and using a separate charger to get the batteries to full charge before reconnecting to the Victron monitor and do a manual syncronization to 100% and see how things go from there.
(c) contact a Victron dealer and/or the battery manufacturer to see what advice they might be able to provide for your specific situation. It may just be a matter of tweaking specific settings for the Aolithium batteries, specifically to get the two apps to work together and provide consistent data.
(Alde: 3020; Refrig: Isotherm Cruise 65 Eleg; Battery: BB 100Ah LiFePO4; Solar: Renogy 220W Portable Suitcase w/ Victron SmartSolar MPPT 75/15 Controller; Victron BMV-712 Battery Monitor w/ Shunt; Pwr Cntr: PD-4135KW2B; EMS: PI-HW30C)
Greg & Marlene (Tucson, AZ)
I put a voltmeter on the batteries and both were at 13.18V (about 70%) so it would seem the BMS is correctly reporting the state of charge.
I went out in the bright sunshine again this morning and found the solar controller reporting the battery voltage as 13.86V (about 100%) and again stuck in absorption mode. I then disabled the solar controller for about 10 seconds then re-enabled it. Interestingly, the solar controller went to bulk mode.
Today I'll try @Bayliss's idea and depower the controller to try the old stop/start solution. I've also been in touch with the Victron supplier for nuCamp and started a thread with them. I'll report back here if anything comes of that as well.
SC stuck in absorption mode
BMS sitting at 70%
SC in bulk mode after disable/reenable
BMS after disable/reenabling SC
SC charge history showing periods of bulk charging mode
I still don't know why the SC sees the batteries as full when the BMS says they're not. Also, I don't understand why disabling the SC then re-enabling it flips the SC to bulk mode for a while, yet not enough to fully charge the batteries.
I'll try depowering the SC today and see if that changes anything.
Glen
I am only adding this comment, because I am not sure if the 13.18V reading is with the battery disconnected and after having "rested."
Good luck!!
(Alde: 3020; Refrig: Isotherm Cruise 65 Eleg; Battery: BB 100Ah LiFePO4; Solar: Renogy 220W Portable Suitcase w/ Victron SmartSolar MPPT 75/15 Controller; Victron BMV-712 Battery Monitor w/ Shunt; Pwr Cntr: PD-4135KW2B; EMS: PI-HW30C)
Greg & Marlene (Tucson, AZ)
It’s uncertain whether it is the same model as yours, so I suggest raising the charge setting to 14.4v, which is common for many LFP batteries.
2018 T@B 320 CS-S; Alde 3020; 4 cyl 2020 Subaru Outback Onyx XT
2018 T@B 320 CS-S; Alde 3020; 4 cyl 2020 Subaru Outback Onyx XT
After waiting a few minutes, I replaced the fuse and low and behold the SC saw the 70% charged battery which agrees with the BMS. When I left the trailer this evening, the SC was in bulk mode and all seems good. My fingers are crossed that tomorrow's sunny day will be spent in bulk mode charging our batteries.
Thank you again all for your ideas and suggestions! I'll update this thread when I confirm the fix tomorrow.
(Alde: 3020; Refrig: Isotherm Cruise 65 Eleg; Battery: BB 100Ah LiFePO4; Solar: Renogy 220W Portable Suitcase w/ Victron SmartSolar MPPT 75/15 Controller; Victron BMV-712 Battery Monitor w/ Shunt; Pwr Cntr: PD-4135KW2B; EMS: PI-HW30C)
Greg & Marlene (Tucson, AZ)
After pulling the fuse for the battery connection to reset the SC, the voltage for both the SC and BMS were the same. As the day went on, the SC stayed in bulk mode but the SC battery charge showed almost full while the BMS was less.
By the end of the day, once again, the battery voltages between BMS and SC were the same. I'm going to track voltages throughout the day tomorrow to see if I get the same behaviour.
Fun.
The SC and BMS agree on the rested battery SOC. There's plenty of solar coming to the SC and the charge state is bulk yet the SC says the batteries are fully charged which they are not.
The batteries seem to be accepting only a couple amps so I'm not making as much progress as I'd expected. I'm certain that just this spring the solar was topping off our batteries without problem so I don't know what has changed since.
I'm very confused but starting to think I should try changing out the solar controller.
Are your batteries wired in "series" or "parallel." The reason I ask is because you most likely had the two 6V batteries wired in series, which allows the two 6V batteries to become 12V. Since you now have two 12V batteries, you want to wire them in parallel so that they remain at 12V/200Ah (rather than 24V/100 Ah.) You can read more about the differences via a Google search.
I'm just wondering if maybe that could the problem, because your solar controller and BMS are set for 12V, but your batteries might be wired to create 24V. Just a thought, because I am running out of ideas to share with you.
Also, I may have missed it in your comments, but did you charge each of the batteries to 100% with a separate lithium-capable charger? If not, do that before reconnecting them to the trailer solar/BMS. You can then do a manual reset to 100% synchronization to see how things go from there.
Finally, have you received any helpful input from nuCamp's Victron supplier? Just curious.
Below is a depiction of the difference between series and parallel wiring, BUT NOTE: Although the wiring is accurately depicted, there is a typographical error in the text below the "Wired in Parallel" heading. The text should read “2 batteries wired in parallel . . . .”
(Alde: 3020; Refrig: Isotherm Cruise 65 Eleg; Battery: BB 100Ah LiFePO4; Solar: Renogy 220W Portable Suitcase w/ Victron SmartSolar MPPT 75/15 Controller; Victron BMV-712 Battery Monitor w/ Shunt; Pwr Cntr: PD-4135KW2B; EMS: PI-HW30C)
Greg & Marlene (Tucson, AZ)
Where are you getting this? Where does the SC say that the batteries are fully charged?
2013 CS-S us@gi
2015 Toyota Tacoma PreRunner Double Cab
You’ll notice that the charging graph of last few days shows that the max voltage reached 14.6v on the occasions that it switched to “float”. That’s a strong indicator that a LiFePO4 battery is full.
2018 T@B 320 CS-S; Alde 3020; 4 cyl 2020 Subaru Outback Onyx XT
Regarding the "shunt," I can see why Victron is asking you about that. If you had one connected in your monitoring system, that would be better for more precise monitoring. Also, one thing that makes it a bit complicated in trying to figure out what is going on is that you are using two different monitoring systems (Victron SmartSolar Controller and the Aolithium app.) Most of us are using the Victron BMV-712, which includes a shunt.
Rather than try to explain it, here is a quick "AI" blurb:
"A shunt in a battery monitoring system serves as a precise current measurement device. It allows the monitor to accurately track the flow of energy into and out of the battery, providing a more accurate state of charge calculation than voltage readings alone. This real-time monitoring is crucial for understanding battery capacity and preventing over-discharge, especially in systems with LiFePO4 batteries."
(Alde: 3020; Refrig: Isotherm Cruise 65 Eleg; Battery: BB 100Ah LiFePO4; Solar: Renogy 220W Portable Suitcase w/ Victron SmartSolar MPPT 75/15 Controller; Victron BMV-712 Battery Monitor w/ Shunt; Pwr Cntr: PD-4135KW2B; EMS: PI-HW30C)
Greg & Marlene (Tucson, AZ)
.
2018 T@B 320 CS-S; Alde 3020; 4 cyl 2020 Subaru Outback Onyx XT
2013 CS-S us@gi
2015 Toyota Tacoma PreRunner Double Cab
2013 CS-S us@gi
2015 Toyota Tacoma PreRunner Double Cab
Ken / 2023 Tab 400 “La Bolita” (29,000+ miles) / 2024 Toyota Sequoia
2025 - 1 Trip - 25 nights - 2 National Parks
To summarize, after removing the fuse to the solar controller battery side found in the passenger side storage locker, the SC is now spending almost all of its time in bulk mode rather than absorption. As a result, I'm slowly approaching full charge as reported by the Aolithium BMS.
Once again, thanks for the assistance.