Just bought a 2020 T@b 400 and the hot water works fine but the heat does not. The white Alde bathroom heater is cold to the touch. My Room Sensor indicator is gray, not blue. Could that be the problem? All other settings appear to be correct (not on Delay, propane lights green). Some of the red plastic water lines near the Alde unit feel cold. Could there be a valve closed somewhere? Thanks!
0 ·
Comments
2020 nuCamp T@B 320S * Jeep Wrangler
(47,171 towing miles through the end of 2024)
Alde System uses City Water Pressure (or the Water Pump) to move hot water from the Alde tank to the sink/shower. For Cabin heat the Alde has a stand-alone Circulation Pump to move the hot glycol.
1] Confirm the Glycol Expansion Tank is at the correct level.
2] Can you hear the Circulation Pump running (or feel it vibrating)
3] Consider resetting the Alde System to factory default conditions.
Control Panel Service Page, RESET button,
Now confirm Cabin Heat is set to a temperature above actual cabin temperature,
Check the Setting - Circulation Pump Screen; confirm it is set to Therm
Therm: The pump is controlled by the room sensor.
This is the normal mode for heat and hot water.
Reference:
TV: '17 Colorado V6 Z71 4x4, Tow Package, GM Brake Controller
Adventures: 56 Nights: 379 Towing Miles 47,220
To the best of my knowledge nüCamp does not install extra cabin temperature sensors.
The only sensor is in the Control Panel.
So make sure your "Setting a room sensor" is not active or set to Auto.
It being grayed out suggests that feature is not available/active.
Let us know when you have had a chance to experiment with the Alde System again.
TV: '17 Colorado V6 Z71 4x4, Tow Package, GM Brake Controller
Adventures: 56 Nights: 379 Towing Miles 47,220
I tried the tilt down, tilt up exercise two times, ran the alde circ pump all the way up high.
I have a flow unit and the rubber tube that comes out of the flow unit to the flo pump and also on to the heat loop, was HOT to the touch and very hard. The rubber hose that goes to the suction of the alde pump was cold to the touch, and squishy... i could pinch it closed and let it spring back open. I vented the kitched heat exchanger (under the sink) and the bathroom heat exchanger (glycol right away, no air).
It seems like there is a blockage in the heat exchanger loop. Has anyone experience a failed check valve (that is the only component downstream of the Alde/Flow unit before the under bed heat exchanger).
Any ideas??
1. I have a 2020 NuCamp Tab 400, with the Alde Flow installed.
2. I operate the Alde with the hot water boost OFF, and the glycol heats up to 172 degrees F, and i do have hotwater. Both glycol rubber hoses from the Alde Unit to the Flow, and the recirc back from the Flow to the Alde Unit are hot - 140 F. The recirc pump from the Flow unit is OFF (wires disconnected), yet there is significant flow back to the Alde unit bypassing the pump, indicating that the "return to Alde" flow resistance is less than the heater loop flow resistance.
3. the Hose from the Flow unit that goes to the heater loop heats up to 90 F, but no higher (suggests to me there is flow blockage in the heater loop). I am pretty sure there is no air in the system. I have done so many tilt up/tilt down cycles and so much venting of heaters that any air has been vented.
4. The Alde recirc pump does appear to run. If i raise the setting to 5 on the pump i can hear it "whirring" and when i turn power to the unit off, the whirring noise stops.
5. From the thread on "Changing out Alde fluid" @BrianZ and @Denny16, there should be a "non-return valve" on the "suction side" of the Flow Circulation pump, but there is not one installed on my system.
6. When i insert the special tool (bent pipe with stopper) into the Vent tank outlet, and Pump glycol into the system, i get a significant pressure buildup in the pump discharge, indicating there is some blockage in the heater loop somewhere.
My planned Next steps:
a. drain glycol from the drain fitting under the trailer.
b. disconnect the hose from the outlet of the flow unit (that also goes to the suction side of the flow circ pump), and visually inspect the hoses to the inlet of the rear heater for crud/foreign material/blockage.
c. if no blockage is noted, then try to pump glycol thru the heater loop from this location (pumping into the rubber hose connected to the inlet side of the rear heater.
d. swap out the Flow Circ pump for the Circ pump for the central heating system that feeds glycol from the heat loop (suction side) into the Alde 3020 unit. (rationale - IF there is a problem with the 3020 unit pump (because it has the most run time), the Flow unit circ pump should fix the issue and i'll know whether i have a bad pump.
@ScottG , @Denny16 and any others... any additional insights or suggestions?
The Alde literature indicates that a valve is on the discharge side of the pump, not the suction side as you noted.
Consider plugging/blocking the Flow Pump to Boiler Line for troubleshooting; force glycol to flow into heater loop to see if problem is the Flow Pump or non-return valve.
TV: '17 Colorado V6 Z71 4x4, Tow Package, GM Brake Controller
Adventures: 56 Nights: 379 Towing Miles 47,220
SUMMARY: the entire heat loop was clogged with crystallized glycol chunks.
the crystals were blocking the glycol flow thru the heat loop so that when I ran the Alde system it just recirced the glycol from the Alde unit to the Alde Flow unit and back, so I had plenty of hot water while freezing my butt off in Northern Idaho.
i disassembled the heat loop, joint by joint, reamed out the piping, and convectors with a flexible “spring wound” cable guide, flushed the rubber connectors in a sink with a wire brush and then dragged a wire brush thru each convector and section of piping I could not physically remove. Pic below shows the tools I used to clear the pipes/convectors.
special thanks to @MuttonChops @ScottG @Sharon_is_SAM and @Bergger for their help during this 10 month journey
May 2024: serviced my Alde unit by flushing the glycol using the tubes, fittings and hand pump described by @ScottG.
Nov 2024: while camping in northern Idaho, the Alde heat worked for 5 days, and then stopped working, though I did have hot water. The vent tank level indicated there was a leak, which quickly depleted the 1 pint of reserve glycol I carried.
upon return to home, I lifted the bed panels to access the Alde unit to try and find the source of the leak, hot glycol was squirting out of the rubber hose to aluminum pipe union that directs glycol from the Alde unit to the flow unit. Upon investigation, I discovered that the aluminum pipe was split and distorted at one end, which prevented a good seal with the rubber tubing (see photos)
CRITICAL MISTAKE: Since I would need to drain the system down to install the replacement aluminum tube, and since I would not be using the trailer or Alde unit anymore that season, I left the glycol partially drained and placed the trailer in storage. Although winter temps did not drop below -15 degrees F referenced in the Alde manual for crystallization point of the 60/40 glycol mix, I suspect the exposure to the air-glycol interface of the partially drained glycol loop, in addition to sub freezing winter temps caused glycol crystallization to occur.
March 2025: installed the replacement aluminum pipe and refilled the glycol side of the system. returned to northern Idaho, living in my trailer during some construction work. The heat worked great for about 4 days, then stopped working, while the hot water continued to work. (In hindsight, during this period, glycol crystals that had formed over the winter were circulated into and accumulated in the heat convectors and associated piping.
April-August 2025: tried various methods to restore the heat loop, tilt the trailer up, tile down vent convectors, measure convector temps while running Alde, all to no avail, but hot water was available the whole time.
finally this past week, I drained the system thru the drain plug underneath the trailer, and noticed an accumulation of crystal sludge in the funnel. When I disconnected the rubber union that directs glycol from the flow unit to the rear connector, it was clogged with crystals. After disassembling a couple more of the easy to reach rubber connectors, and finding clogging in each place with some pipes nearly 100% blocked, I began a complete disassembly, and clearing of crystal residue. The hardest convector to get to was the one under/behind the front right hand bench seat. The floor of the storage compartment was screwed form the inaccessible bottom! When I reassembled the bench, I drilled a finger hole in the floor and did not screw it in place, in case I ever have to take it apart again!
Happy to say my Alde heat is working again. The system is great…when it works, but so frustrating when it gets finicky. Regardless, I still like my NuCamp T@b 400 trailer.