Confused with the position of the Alde bypass valve 2019 Tab 320 S
hello everyone, we purchased a used 2019 tab 320 S. The dealer de winterized it and we camped for one night to test all systems. We had full hook ups. Water was coming out hot at times, albeit fluctuating…….. When we got home, we noticed that the Alde Bypass valve was in the “open” position (parallel to the lines). This is the opposite of what the photos in the manual show for camping season mode. But we did have hot water.
We were confused so we called customer service. They said the valve should be in the “open” position to allow water to flow into the Alde tank. Again, this is opposite to what the manual says. Has anyone experienced this? Is the manual wrong? I’m attaching a picture of my system and the picture shown in the manual.
we are new to this and we don’t want to cause any damage.
2019 T@b 320 S 2nd owner
Nissan Pathfinder
Central MA
«1
    pthomas745 Administrator, Moderator Posts: 4,700
    edited May 21
    When you said the hot water was "fluctuating", that was the basic clue back in the day that the "Bypass" valve was open. Owners would have hot water for a few seconds, then cold water for a while, then a little more hot water, etc. Maybe a factor here is you being on city water, and the extra flow from that connection made a difference.
    You are correct: that "bypass" should be closed. The actual duty of "preventing sanitizing or winterizing solutions from getting to the Alde hot water tank" is performed by the two valves on the hot and cold lines heading into the Alde.
    The"bypass", when open, simply allows those liquids you want to keep out of the Alde to circulate properly around the plumbing back to the faucets.
    So, try this for yourself, while using water from the fresh water tank and the pump, with the Bypass Valve "open". I bet you get the "fluctuating" water situation.
    And, good for you for having your manuals and…using them!
    And, welcome to the Forums!
  • Voyager
    Voyager Member Posts: 63
    edited May 22
    thank you @pthomas745 for your quick response. We just tried closing the valve (perpendicular to the lines) and we did not have water in the hot line at the faucet. So, at least in this particular camper, the bypass valve should stay in the open position during camping season (contrary to what the manual shows). Thanks again!
    Nissan Pathfinder
    Central MA
    MuttonChops Member Posts: 2,079
    @Voyager , Sorry, but you are incorrect as the ByPass-Valve Must Be Closed for camping season to get real Hot Water for more than a few seconds.
    Assuming the first picture you posted is your TAB:
    Considering your TAB is a yr-2019 . . . the most common reason for no hot water is the TMV mixing value is clogged, jammed and needs to be serviced. Every few years the TMV should be cleaned and lubricated Something That Is Not Covered in any of the nuCamp manuals.
    This forum has a document in the Resources Section outlining how to service the TMV
    LK550 Mixing Valve Operation and Servicing
  • Voyager
    Thank you for responding, when we close the bypass valve no water comes out of the hot water faucet. That is indeed the photo of my camper. Nucamp customer support said it should be open. I will however review the mixing valve and try again. Thanks for the link.
    Nissan Pathfinder
    Central MA
  • Bayliss
    Bayliss Member Posts: 1,534
    @Voyager , I agree with @MuttonChops. I think nuCamp Customer Support may be misinterpreting what you are experiencing.
    I may be misunderstanding what is going on as well, BUT, before you do any adjusting to the mixing valve, is it possible that your Alde hot water tank is not filled (because the bypass valve remaining open is not allowing sufficient water to flow through the cold water line to fill the tank?).
    To find out, close the bypass valve, but leave all the other valves set as depicted in the photo posted by @MuttonChops. Then, connect a fresh water hose (with pressure regulator attached) to the fresh water inlet on the side of the trailer. Turn on the hose to energize/pressurize the water lines and fill the Alde tank. You don't necessarily need to turn the hose on full blast, at least initially, but sufficiently enough to pressurize the water lines.
    To allow the water to be pulled into the Alde tank, open the cold and hot water faucets at your kitchen sink, just a bit, to bleed/pull the air out of the water lines, which should in turn allow the water to start flowing through the lines to the faucet.
    Gradually further open the cold and/or hot water valves at the sink to increase the amount of air and water flow as the water lines fully pressurize. Once the "sputtering" stops, and you have a constant/smooth flow of water running through the faucet, your Alde tank should be filled. You will probably need to open the shower and toilet valves too to get water flowing through those lines as well.
    If all goes well, and your Alde tank is full and the water lines pressurized, it should just be a matter of heating the water in the Alde tank to see if hot water starts flowing at a good temp.
    Greg & Marlene (Tucson, AZ)
  • Grumpy_G
    Grumpy_G Member Posts: 787
    Check if you have hot water at the outdoor shower with the bypass valve closed. That will tell if there's an issue upstream of the bypass valve.
  • Voyager
    thank you all. I think you guys might be right since what you are saying is consistent with what the manual says, bypass valve closed for camping season. @Bayliss, we left the valve open as in the photo, filled the fresh tank, turned pump on, open faucets and wait till the pump shut off. We could feel water getting into the Alde. Then we opened the Alde drain valve to confirm and, indeed, water did drain out. So something is going on. I am not sure that I feel confident to check the mixing valve myself as @MuttonChops suggested though. We are camping this weekend so I may leave the hot water off and then take it to the dealer to check. But that scenario makes more sense than leaving the bypass valve open, and it would explain more things. So I will bring it up to the service provider.
    @Grumpy_G , we do not have the outdoor shower. It needs to be replaced because it was leaking. It’s on the mail.
    I will come back to let you all know. Thank you so much!
    Nissan Pathfinder
    Central MA
  • Voyager
    this is the email exchange with Nucamp
    Nissan Pathfinder
    Central MA
  • Bayliss
    @Voyager, thanks for the additional info.
    Based on what you wrote, it sounds like you are filling your fresh water storage tank (via the fresh water fill port) and then using the water pump to transfer water from the fresh water storage tank to the Alde tank.
    That is definitely necessary IF you do not have access to a fresh water supply connection from your house, or at a campground. However, if you do have access to a water connection at your house or a campground, that will be a faster and more efficient way to fill your Alde tank. It does not involve/require using the water pump.
    The primary advantages are that (1) you will not be depleting your fresh water tank supply (by at least 2 gallons, but likely more if you are running the pump until it stops filling the Alde, because you are also filling/pressurizing all the water lines inside the trailer as well), and (2) you are not using your 12V battery power to run the pump (assuming you are not hooked up to electricity).
    Regardless of the method used, you still need to close the bypass valve so the cold water is directed to the Alde tank.
    Also, although you indicate that there was water in your Alde tank, if you only tested that (presumably, by opening the yellow flapper) for a brief period, it is possible that you are only accessing residual water in the Alde tank, which could be present because "some" water made it inside the Alde tank, which potentially could happen even if the bypass valve was left open during the filling process.
    Anyway, enjoy your camping trip this weekend. I'm be looking forward to see how it all works out. I always learn something new from individual experiences discussed on this Forum, which is valuable information when I encounter similar issues. We truly have a dedicated group of T@B owners.
  • Grumpy_G
    Warning: Sarcasm follows….
    You got an answer from a "Customer Experience Manager" and a quick google search shows his background is in sales and marketing, including a stint as an account rep for Kellogs.
    To be fair a total of three valves need to be changed to switch between winterizing and camping. He is correct that the valves to and from the Alde need to be open to have hot water, but the bypass valve needs to be closed.
  • Voyager
    @Bayliss, yes, I know using the city water connection is better, we were just trying things out and our campsite for this weekend doesn’t have water hookups. And yes, we opened the yellow valve. But you may still be right that it’s only residual water. Thanks again, I will keep you guys posted.
    Nissan Pathfinder
    Central MA
  • Voyager
    @Grumpy_G clever of you to google him!
    Nissan Pathfinder
    Central MA
  • Voyager
    edited May 22
    @pthomas745, @Bayliss, @MuttonChops, @Grumpy_G
    This is my first post on this forum. I am impressed by the time and dedication you all put into replying. 👏
    Nissan Pathfinder
    Central MA
  • Mickerly
    Mickerly Member Posts: 512
    I have a 2018 like yours. The last time this water was installed in the 2019 model year. In 2020 they changed to the newer system.
    Because of the Alde design, you can't do any harm running it with or without water. The electric elements are in the glycol.
    Another thing to keep an eye on is the outside shower. Make sure both knobs are off. If you leave them on, the hot and cold will mix through the valve assembly. All faucets in the trailer will have medium temperature water.
    2018 320CS-S
    "Just Enough"
  • Voyager
    @Bayliss I checked again how much water came out of the Alde. I put a bucket under the Alde drain, opened the yellow flapper and collected the water. What came out was about 5L which is a bit over a gallon. What are your thoughts?
    Nissan Pathfinder
    Central MA
  • Voyager
    @Mickerly that’s good to know. I will check the outdoor shower knobs too. Thank you!
    Nissan Pathfinder
    Central MA
  • Bayliss
    edited May 22
    @Voyager, I'm not sure what to think, because 1 gallon is just under what the Alde tank holds (approx. 2.2 gallons, I believe). Before doing that, did you feel that the Alde tank was likely full (i.e., you went through the process to fill the Alde tank and pressurized the water lines)?
    If so, if I were troubleshooting this, I would next put the bucket back under the yellow flapper. Open the hot an cold water valves all the way at your kitchen sink and then open the yellow flapper valve to see if any more water drains out. IF there was a full tank, and you only got 1/2 to drain using the yellow flapper alone, maybe opening the valves at the sink will reduce any vacuum present and increase the flow, emptying the rest of the tank. Worth a try.
    FWIW, I recall some past discussion by @ScottG (who may chime in) regarding the fact that opening the cold water low-point drain valve can also drain the Alde hot water tank. Again, draining the low point drains (hot or cold), such as when winterizing or sanitizing the plumbing system, is more efficient if you open the valves at the sink (I also open the shower valves) to help release any vacuum that may be present in the water lines. This won't necessarily help resolve whether the Alde tank still has water in it. However, if more than a gallon comes out, that would likely be a good indicator that most of the water came from the Alde tank. If nothing else, just good info to know.
    However the situation resolves, it will be helpful information for all those interested in what you are dealing with.
    UPDATE TO ABOVE: I found the following (from the Alde manual) in my Alde notes (basically confirms my suggestion about the vacuum in the water lines):
    Per Alde manual, to drain the Alde tank:
    1. Switch off the fresh water pump.
    2. Open all water taps.
    3. Open the safety/drain valve by lifting the yellow lever.
    4. The hot water tank in the heating system will now drain directly below the vehicle through the safety/drain valve (i.e., yellow flapper) hose. Check that all the water is emptied out (2.2 gallons). Leave the yellow flapper valve in the open position until the next time the boiler is used, so that it can air out.
  • Voyager
    edited May 23
    @Bayliss , I opened the faucet, then the yellow flapper, and got maybe another quart out of the tank. I need to run more tests with the bypass valve closed, maybe I didn’t wait long enough for the tank to fill.
    Nissan Pathfinder
    Central MA
  • Voyager
    @MuttonChops , I think we have a different mixing valve. Can you kindly please confirm? Are the connections correct? Thank you.
    Nissan Pathfinder
    Central MA
  • Bayliss
    edited May 23
    @Voyager, it looks like you have the "Speedfit Thermostatic Mixing Valve" (TMV), which Truma-Alde started using with newer systems. I am surprised that you have it on a 2019 320 S, because the mixing valve on my 2019 320 S (and I am guessing on @MuttonChops' 2018 320 S as well) is different.
    See this discussion thread for some helpful info, BUT be sure to read the corrected/updated info in the first post re how to adjust the valve:
    If you encounter any adjustment issues, you can always contact Truma (Alde) for assistance.
    @Voyager I agree with @Bayliss that it appears an earlier owner replaced the original TMV [black cap LK550] with the newer Adle Branded [red cap] TMV . . . most likely because the LK550 needed maintenance.
    The newer TMV includes a screen filter on the cold water input side.
    Several owners have reported the screen being clogged, retricting or stopping water flow.
    The Alde TMV appears to be a cheaper (IMHO) re-branded Cash Acme HG110-HX unit which has far less web-available information than the LK550. At this time no TAB owner has provided an overview of the unit at a level near/equal/better then the LK550 Document in our resources section.
    That said . . . basic operation and parts are similar to the LK550 with the addition of that Screen Filter and perhaps some flow direction check-valve parts.
    If you are getting water flow from the Hot Side of faucets.
    But only get a short blast or no Hot water then the TMV needs attention.
    If you have zero Hot Water Side Flow . . . then something else is wrong.
  • Voyager
    edited May 29
    @Bayliss @MuttonChops I believe the dealership where we bought it had to replace it after the inspection. But I don’t have a lot of confidence in them.
    Nissan Pathfinder
    Central MA
  • Bayliss
    edited May 24
    @Voyager, on the brighter side, IF the TMV is the problem, the dealer should fix/replace it without charge to you. 😁 Unfortunately, a lot of dealers don't fully understand the systems in T@B RVs, which is why there are so many DIYers on this Forum. Lots of knowledge to share, often gained by trial and error.
    edited May 25
    I was noodling around looking at mixing valves yesterday (I'm sure everyone does this sort of thing, amirite?) I know that a couple of owners have simply yanked these convoluted "thermostatic" valves from the trailer and replaced them with just ordinary "adjust with a screwdriver" mixing valves.
    When I searched Amazon for the Cash Acme valve Muttonchops listed above, I ran across this "Tremax" valve. One of few reviews had a picture of this valve plumbed into a 400. It would seem there are many different mixing valves that can easily be adapted to the Tabs. There doesn't seem to be much reason to stay with the valves provided by NuCamp if you have some simple skills to put in something that might perform better.
    TreMax Mixing Valve Amazon
  • Voyager
    edited May 29
    update
    We are back from our 4 day trip. We closed the bypass valve to the camping season position. Water goes into the Alde and is heated, but no water comes out of the hot water faucets, either sink or shower. There was another tab at the campground. Owner was very kind to come around and check but he couldn’t determine what the problem is. He suggested maybe an air bubble somewhere. Mixing valve was indeed replaced by the dealer in November, so it is brand new. Dealer suggested there may be some plastic shavings clogging the screen filter in the valve. I have to figure out how to access it. Suggestions welcomed 🙂
    And also now the Alde panel control for hot water goes straight to booster mode. I cannot set it to normal (the half way point). It was working fine for 2 days. We unplugged the camper hoping it would reset but didn’t. So, another issue to work around. Any ideas?
    We don’t really mind not having hot water, but come fall, it would be nice to have it.
    we may need to bring it in to have it checked………..
    Nissan Pathfinder
    Central MA
  • Voyager
    @Bayliss you are right but the dealer where we bought it is a bit far and I don’t really trust them. The Nucamp dealer is much closer to home and should know how to fix them (I assume). So if we cannot figure it out, I rather take it there and pay.
    Nissan Pathfinder
    Central MA
  • Bayliss
    edited May 29
    @Voyager, what area do you live in. Just curious, because you mentioned "the nuCamp dealer". Actually, you might want to add your trailer model and the general area you live in your signature line. That is often helpful info.
    Also, out of curiosity, what did the selling dealer say as far as "why" the mixing valve needed to be replaced? That might be helpful "troubleshooting" information. The first thing I do when trying to figure out why I suddenly encounter a problem is to think back to what I last did that may have contributed/caused the problem. Often times, that is very enlightening.
    With regard to your latest development (i.e., no hot water making it to the faucets), I do not have a specific answer for you. However, plastic shavings (usually introduced due to lack of care used during the original construction process) do at times cause drainage problems. I have encountered that with my fresh water tank, but other owners have posted about similar incidents.
    Thinking about all of this a bit further, although it likely is not a factor in your current issue, take a look at the below discussion thread. I suggest that you read through the entire discussion, but what is good to know is the information posted by @Paul1959 in November 2021. In that discussion thread, I posted a photo of my hot water connection at the Alde tank. Based on the info provided by @Paul1959, mine apparently was installed by the factory in the wrong orientation. I do not have immediate access to my trailer to take a look at its current configuration, but I do not recall re-orienting it, most likely because of a lack of sufficient slack in the hot water out PEX line and/or air vent line at that location. Regardless, I have never had an issue draining my Alde tank, but the information is good to be aware of.
    With regard to the orientation of that hot water connection, in addition to the depictions of the orientation of that "Fresh Water OUT" valve posted in the above discussion thread, the below diagram also shows the orientation of that red valve to be at a slight angle. Thus, it really is not clear whether the "slight angle" or "vertical" orientation of the air vent (connection to the clear tube) is better, but positioning at a slight angle tends to make sense to me, but I'm no engineer.
    AND, one more thought…………….it may be time to give Alde/Truma a call to see what suggestions they have to offer.
  • Grumpy_G
    Let's focus on figuring out where the problem is. Confirm: there is no water coming out of the faucets when set to full hot ? If so you don't even need to have the Alde turned on because it's a water delivery problem, not a water temperature problem.
    Above I suggested to check if there is hot water at the outside shower and for some reason you can't test that but there is another hot water outlet near the Alde system: The hot water side drain for winterizing. So with the water pump on (no external water supply), valves in normal operating positions if you open the drain valve it should behave like a regular faucet. Water should come out below the trailer and the water pump should start running. If yes: Problem is in the lines going towards the front of the trailer. If no: Work back towards the Alde. Start disconnecting the push-connect junctions until water starts flowing.
  • Bayliss
    Good troubleshooting points by @Grumpy_G. 👏
    @Voyager, I just stumbled upon this gem of information in my Alde notes. (I'm not positive, but some of the info may have been originally posted by @Sharon_is_Sam" back in 2019…….a very reliable source). It may resolve your hot water "Boost" question:
    "If the Alde pump is set to “Cont” (i.e., continuous) circulation [as opposed to “Therm” (i.e., thermostat) regulated], you cannot choose the partial shaded option. [@Bayliss NOTE : I discovered this myself in Sept 2024. I figured out that when nuCamp did our glycol exchange on 03-30-2023, they set the pump to “Cont” and never returned it to “Therm.” Because of that, when I wanted to heat the hot water for a shower, the shaded triangle was fully shaded and I could not use the partial shaded option.] While using “Therm,” you can choose the boost (i.e., fully-shaded icon), which stops the glycol circulation for 30 minutes and allows the water to get extra hot for taking a shower.  If you keep the pump setting in the “Therm” mode, you can adjust your water temperature to partial shade OR use the boost option when desired."  [NOTE: Only use “Cont“ (i.e., continuous) for troubleshooting, such as may be needed in conjunction with bleeding air from the glycol lines, BUT do not have the pump “on” when you open a bleeder valve, because that may introduce air into the glycol lines.]
  • Voyager
    thank you @Bayliss, I will check that. When the other T@b owner came to check, he touched the panel. I noticed the issue right after. He may have switched it.
    That diagram of the Alde is very helpful. The mixing valve was leaking badly they said, so they replaced it.
    @Grumpy_G outdoor shower was leaking so they are sending us a new shower kit. I will try your suggestion, thank you very much!
    Nissan Pathfinder
    Central MA
